IPC 1110.4 Minimum number of roof drains states that Not less than two roof drains shall be installed in roof areas 10,000 square feet (929 m2) or less and not less than four roof drains shall be installed in roofs over 10,000 square feet (929 m2) in area.
My question to the forum is weather or not secondary (emergency) roof drains per 1108 count towards the minimum number of roof drains? As an example for discussion, I have a 5000sf low slope membrane roof pitched to (1) primary roof drain, several feet away from the primary roof drain is an emergency over flow roof drain. Per section 1110.4 I am required a minimum of (2) roof drains as the roof area is below 10,000sf, is my design code compliant? Or do I need to provide (2) primary roof drains and (2) overflow drains?
My question to the forum is weather or not secondary (emergency) roof drains per 1108 count towards the minimum number of roof drains? As an example for discussion, I have a 5000sf low slope membrane roof pitched to (1) primary roof drain, several feet away from the primary roof drain is an emergency over flow roof drain. Per section 1110.4 I am required a minimum of (2) roof drains as the roof area is below 10,000sf, is my design code compliant? Or do I need to provide (2) primary roof drains and (2) overflow drains?