• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

2018 IMC warehouse ventilation rates

HVACQuestions

Registered User
Joined
Sep 23, 2019
Messages
23
Location
02210
For the IMC 2018 warehouse ventilation rates, they specity 0.06 cfm/sf, which has been the standard. but now they've added a 10 cfm/person requirement, which is new, but the occupant density column is blank. so how do i establish a minimum ventilation rate?
 
Figure out the occupancy per IBC TABLE 1004.5
MAXIMUM FLOOR AREA ALLOWANCES PER OCCUPANT
500 gross SF per person for Warehouse
Then figure out your total
 