Mr. Inspector
SAWHORSE
Odd that this in the Article 600 Electric Signs and Outline Lighting. Who would think of looking for it if you were not looking at a sign. I would think it should be in Article 210 Branch Circuits. No exceptions. The second paragraph is from the NEC Handbook.
600.5 Branch Circuits.
(A) Required Branch Circuit. Each commercial building and each commercial occupancy accessible to
pedestrians shall be provided with at least one outlet in an accessible location at each entrance.
to each tenant space for sign or outline lighting system use. The outlet(s) shall be supplied by a
branch circuit rated at least 20 amperes that supplies no other load. Service hallways or corridors
shall not be considered accessible to pedestrians.
This requirement is not contingent on whether an electric sign will be installed at the time an
occupant moves in, since it is not uncommon to install an electric sign after the space is occupied.
or when a new occupant moves into an existing space.
I would like what other electrical plan reviewers and inspectors and also any architects answer my questions or have any comments.
1. Is this always required in all new commercial buildings even if there are no signs on the plans? (Usually the sign company gets their own permit after the permit was already issued for the building or after the C O.)
2. Is this required for alterations in an existing commercial building?
3. Is it required when there is change of occupancy?
4. is this required even if no electrical work is being done in a commercial building?
5. If the entrance to the tenant space is inside a hall or mall is it still required.
6. Is it only a requirement if installing an electrical sign somewhere on the property?
7. If there are multiple buildings on the same site for the same tenant is this required on every entrance for every building?
8. Would it be required at employee and loading entrances?
600.5 Branch Circuits.
(A) Required Branch Circuit. Each commercial building and each commercial occupancy accessible to
pedestrians shall be provided with at least one outlet in an accessible location at each entrance.
to each tenant space for sign or outline lighting system use. The outlet(s) shall be supplied by a
branch circuit rated at least 20 amperes that supplies no other load. Service hallways or corridors
shall not be considered accessible to pedestrians.
This requirement is not contingent on whether an electric sign will be installed at the time an
occupant moves in, since it is not uncommon to install an electric sign after the space is occupied.
or when a new occupant moves into an existing space.
I would like what other electrical plan reviewers and inspectors and also any architects answer my questions or have any comments.
1. Is this always required in all new commercial buildings even if there are no signs on the plans? (Usually the sign company gets their own permit after the permit was already issued for the building or after the C O.)
2. Is this required for alterations in an existing commercial building?
3. Is it required when there is change of occupancy?
4. is this required even if no electrical work is being done in a commercial building?
5. If the entrance to the tenant space is inside a hall or mall is it still required.
6. Is it only a requirement if installing an electrical sign somewhere on the property?
7. If there are multiple buildings on the same site for the same tenant is this required on every entrance for every building?
8. Would it be required at employee and loading entrances?
Last edited: