aarondahl
REGISTERED
Howdy!
I have a car dealership project with a service drive canopy attached to the service building on one side, then open on the other 3 sides. The sales building is ~5' from the opposite side of the canopy. We have confirmed the canopy complies with Section 3105. The AHJ is contending this canopy is an extension of the service building and we must "demonstrate compliance with Section 705.3". I do not consider this as a reasonable intepretation of the code. There are no walls to the canopy, they are trying to enforce a firewall on the sales building (which is mostly glass). I am trying to determine my best approach to respond.
Thanks in advance.
I have a car dealership project with a service drive canopy attached to the service building on one side, then open on the other 3 sides. The sales building is ~5' from the opposite side of the canopy. We have confirmed the canopy complies with Section 3105. The AHJ is contending this canopy is an extension of the service building and we must "demonstrate compliance with Section 705.3". I do not consider this as a reasonable intepretation of the code. There are no walls to the canopy, they are trying to enforce a firewall on the sales building (which is mostly glass). I am trying to determine my best approach to respond.