Greetings. We are working on a design of a small office park (B Occupancy) and hung up on the following exemption.
705.8.1
The current site plan places each rectangular shaped building (about 1,900 sqft each building) ,12' apart in a single row (no side soffits..). The project is comprised of an exterior insulated CMU block system (non-load bearing.. 2.7 hr rated), interior steel columns / wideflanges / steel joists / metal corrugated deck with standing seam roof system that is not dependent on the exterior walls. (Type II Construction - non-sprinkled).
Would these building meet this exemption and allow unlimited unprotected openings?
The client would like to place several windows on the side wall of the buildings (windows basically facing each other between each building) and we are wondering if we can exceed the 15% allowance (705.8).
Thank you for your feedback in advanced.
705.8.1
- In other than Group H occupancies, unlimited unprotected openings are permitted in the first story above grade plane where the wall faces one of the following:
- A street and has a fire separation distance of more than 15 feet (4572 mm).
- An unoccupied space. The unoccupied space shall be on the same lot or dedicated for public use, shall be not less than 30 feet (9144 mm) in width and shall have access from a street by a posted fire lane in accordance with the International Fire Code.
- Buildings whose exterior bearing walls, exterior nonbearing walls and exterior primary structural frame are not required to be fire-resistance rated shall be permitted to have unlimited unprotected openings.
The current site plan places each rectangular shaped building (about 1,900 sqft each building) ,12' apart in a single row (no side soffits..). The project is comprised of an exterior insulated CMU block system (non-load bearing.. 2.7 hr rated), interior steel columns / wideflanges / steel joists / metal corrugated deck with standing seam roof system that is not dependent on the exterior walls. (Type II Construction - non-sprinkled).
Would these building meet this exemption and allow unlimited unprotected openings?
The client would like to place several windows on the side wall of the buildings (windows basically facing each other between each building) and we are wondering if we can exceed the 15% allowance (705.8).
Thank you for your feedback in advanced.