Section 318.7.9 of the 2024 IRC states, in it's entirety, that “Alterations to existing stairs shall not be required to comply with the requirements of this code where the existing space and construction does not allow a reduction in pitch or slope.”

And that is it. Nowhere does it specify, or adjacent sections specify, that the requirements of the code you are not required to comply with are limited to slope and head height.

As written, do you agree that this would mean that you could not enforce handrails, guardrails, risers with more than 3/8" variance, egress width, fire protection on the bottom of the stairs, etc.? That wasn't the intent, surely.

I am asking because we are going through code adoption and we could amend this section a little to meet intent without compromising other requirements.
 
As written, do you agree that this would mean that you could not enforce handrails, guardrails, risers with more than 3/8" variance, egress width, fire protection on the bottom of the stairs, etc.? That wasn't the intent, surely.
Correct...they don't want you to have to blow the house apart to "fix" the rise and run....
 
  • Like
Reactions: SDS
As written, do you agree that this would mean that you could not enforce handrails, guardrails, risers with more than 3/8" variance, egress width, fire protection on the bottom of the stairs, etc.? That wasn't the intent, surely.

I am asking because we are going through code adoption and we could amend this section a little to meet intent without compromising other requirements.

No, I don't agree. The intent is to not require a replacement stair to be a 7:11 stair where the original was an 8:9 stair. Keeping the new [replacement] stair within the existing footprint doesn't prevent providing compliant handrails, guards, protected soffit, and limiting variations in riser height to 3/8".

If that's not clear, then your jurisdiction probably should amend it in adoption.
 
It must just be me. "Intent" is not code, but at some point, a building official just needs to grow a spine and make the right things happen.
 