I think we've covered this in previous threads some years ago. Measuring on a path the hugs the perimeter wall instead of going on a diagonal may well be a best practice, but the current code minimum is simply to measure along a "natural and unobstructed path". Unless you are going to demand an additional furnishings layout as part of the plan check, I don't see how the diagonal path through the Fire Chief's office as shown on the plan can be construed as anything other than "natural and unobstructed".In my opinion, the route from the Fire Chief's office does not comply. Diagonally through the office would not be acceptable.
In my understanding, "horizontal" refers to walking horizontally existing across a floor, and "vertical" refers to descending or ascending on stairs or ramps.The code states horizontal and vertical egress travel. That would eliminate diagonals in my mind. We only measure travel distance with right angles. Sometimes a furniture layout can be beneficial. We typically include furniture on the egress plans for clarity
How can you show the 'natural and unobstructed path' without showing furniture on the plan?I think we've covered this in previous threads some years ago. Measuring on a path the hugs the perimeter wall instead of going on a diagonal may well be a best practice, but the current code minimum is simply to measure along a "natural and unobstructed path". Unless you are going to demand an additional furnishings layout as part of the plan check, I don't see how the diagonal path through the Fire Chief's office as shown on the plan can be construed as anything other than "natural and unobstructed".
The old 1997 UBC used to be even more explicit about furniture not being considered when computing travel distance, as it was already factored into account when the code was approved:
View attachment 10126
This changed sometime around the 2006 IBC (California did a pause through a few code cycles, so I'm not sure exactly when it changed), and it read like this up through the 2015 IBC:
View attachment 10124
Latest change 2018 IBC updated "story" to "room, area or space":
View attachment 10125
Do you enforce the placement of furniture in a building in perpetuity?How can you show the 'natural and unobstructed path' without showing furniture on the plan?
For fixed assembly seating the appropriate pathways should be self-evident. For non-fixed or undefined spaces, the point of the commentary is to have you make the safer assumption which would result in the longer path. In all but very unusually shaped spaces that would be following the walls. The actual condition in use maybe shorter, but we should never assume that from the start for our designs. In the example of a high school gym, in most cases you probably could travel diagonally across an open basketball court. But when the school decides to lay out chairs there and use it for an assembly or a graduation ceremony, that is no longer the case.So at least the commentary suggests the along the wall if furniture is not known. Both fixed and non-fixed assembly seating, often in non-rectilinear spaces, often would not lend itself to the along the wall measuring. I also wondered about a high school gym, and not going diagonally across the court in an emergency egress. Not to mention other non-rectilinear spaces.
View attachment 10128
NFPA does not limit measuring travel distance to "horizontal and vertical egress travel".
agreed, I could easily argue either way. That is why a furniture plan is beneficial to be able to show a diagonal path. Many rooms typically have an orthogonal path inherent. that is typically what we have and show. Measuring the egress travel down a stair parallel to the stringers is appropriate clearly.In my understanding, "horizontal" refers to walking horizontally existing across a floor, and "vertical" refers to descending or ascending on stairs or ramps.
I don't think it refers to horizontal and vertical lines on a 2-dimensional page of plans, which after all is just an abstraction of the actual building.
(If that were the case, then no one would be allowed to build any curved walls or anything other than an orthogonal room).
Also, as I look at the pixels on my screen, a diagonal line is actually made up of a lot of very small vertical and horizontal steps.
The commentary in IBC is clear that you should assume furniture precludes a diagonal path, and instead use rectilinear ones around the perimeter. (1017.2, and Figure 1017.3(2)
View attachment 10127
Just want to point out that the CC commentary is just a staff opinion, and not code. Just this year I had a building department use commentary to require something that I knew was not required. I assembled the history of that section, including my original proposal and substantiation and committed and hearing testimony, and staff agreed the commentary was wrong. Not even suggesting that's the case here.The commentary in IBC is clear that you should assume furniture precludes a diagonal path, and instead use rectilinear ones around the perimeter. (1017.2, and Figure 1017.3(2)
View attachment 10127