I'm working on a renovation/change of use of a two story building with a B occupancy, per the 2021 IBC. The first floor is around 5,000 sf and will have 3 exits doors. The second floor is only 500 sf and is served by a single existing exit access stair. I'm slightly confused on whether this 2nd story needs to comply with table 1006.3.4(2) Stories With One Exit or Access to One Exit
Per 1006.3.3, "Each story and occupied roof shall have the minimum number of separate and distinct exits, or access to exits." Two exits required in this case.
The second floor has access to two exits doors on the first floor that comply with exit access travel distance and common path of egress travel. Does that mean this story this complies with 1006.3.3, even though it only has one exit access stair? I can comply with table 1006.3.4(2)., but I would need to construct a small 1 hour rated exit passageway leading to the nearest exit discharge, in order to comply with the reduced exit access travel distance of 75'. I don't want to do that unless it's necessary.
Per 1006.3.3, "Each story and occupied roof shall have the minimum number of separate and distinct exits, or access to exits." Two exits required in this case.
The second floor has access to two exits doors on the first floor that comply with exit access travel distance and common path of egress travel. Does that mean this story this complies with 1006.3.3, even though it only has one exit access stair? I can comply with table 1006.3.4(2)., but I would need to construct a small 1 hour rated exit passageway leading to the nearest exit discharge, in order to comply with the reduced exit access travel distance of 75'. I don't want to do that unless it's necessary.