Sawhorse
Applicable Code: 2006 IBCSection 705.3 (or whatever section relates to buildings on the same lot)New buildings (no existing buildings - all new)Type VB / Nonsprinkled.Given that there are three buildings - similar to what is shown in the illustration - what commentary reference can you provide that makes it clear the the imaginary line does NOT necessarily need to be exactly in the middle of the building structures?Please note that the combined aggregate total divided by the base allowable area is equal to 1.085 (over the allowable limit). Unless I am missing some allowable area increase for opening separation - as if the three buildings could take advantage of a 75% +/- increase around the group perimeter.Again, my main question is with regards to the arbitrary location of the imaginary line.Thank you,ICC Certified Plan ReviewerNFPA Certified Fire Plan Examiner