Morning all,
Last year when I remodeled my laundry room cabinets and went to (1) combined washer/dryer which doesn't need a 30amp 220, nor vent I just left the old dryer plug as is.
Looking for another circuit on the counter I thought about the 10ga 4 wire sitting in that box not being used.
Is there anything within the NEC that would not allow me to remove the wires in the panel and connect the white/black to the neutral and a 20amp breaker and cap the red.
And then cap the red in the box in the room and wire pigtails to the white, black & ground and connect it to a 20amp duplex outlet and put the cover back on?
I would note the breaker in the panel and with a wire tag on the wire in the panel.
But, am I going off the reservation with this thought to gain another circuit on the counter?
Thank you for the input