3304.7.4 Combustible storage
mtlogcabin
Big Sky Country
2009 IFC
3304.7.4 Combustible storage.
Combustible materials shall not be stored within 50 feet (15 240 mm) of magazines.
New proposed 42,000 sq ft sporting goods store, They will have 2 magazine storage containers 2.2 ft X 4 ft x 6ft High. They will be located in the receiving/storage area of the store which is mostly combustible materials.
Does this section apply to indoor magazines or outdoor or both?
Seems hard to comply with the requirement they be located within 10 ft of an exterior door and at least 10 ft apart unless they are in a room seperated from the combustible storage. So I am thinking this is for outdoor magazines.
3304.1 General. Storage of explosives and explosive materials, small arms ammunition, small arms primers, propellant-actuated cartridges and smokeless propellants in magazines shall comply with the provisions of this section.
3304.5.1.1 Use. The use of indoor magazines for storage of explosives and explosive materials shall be limited to occupancies of Group F, H, M or S, and research and development laboratories.
Did you look at all of 3306.5????????
Are the magazines even required??? If not should be good to go