mtlogcabin
SAWHORSE
2009 IFC
3304.7.4 Combustible storage.
Combustible materials shall not be stored within 50 feet (15 240 mm) of magazines.
New proposed 42,000 sq ft sporting goods store, They will have 2 magazine storage containers 2.2 ft X 4 ft x 6ft High. They will be located in the receiving/storage area of the store which is mostly combustible materials.
Does this section apply to indoor magazines or outdoor or both?
Seems hard to comply with the requirement they be located within 10 ft of an exterior door and at least 10 ft apart unless they are in a room seperated from the combustible storage. So I am thinking this is for outdoor magazines.
3304.7.4 Combustible storage.
Combustible materials shall not be stored within 50 feet (15 240 mm) of magazines.
New proposed 42,000 sq ft sporting goods store, They will have 2 magazine storage containers 2.2 ft X 4 ft x 6ft High. They will be located in the receiving/storage area of the store which is mostly combustible materials.
Does this section apply to indoor magazines or outdoor or both?
Seems hard to comply with the requirement they be located within 10 ft of an exterior door and at least 10 ft apart unless they are in a room seperated from the combustible storage. So I am thinking this is for outdoor magazines.