3x2x1-1/2” handy box with 14/3.

jar546

CBO
Joined
Oct 16, 2009
Messages
12,759
Location
Not where I really want to be
I had an installation today where they brought MC cable, 14/3 into an inch and a half handy box. It is supposed to have a switch in it. Is this code compliant for box fill?

can you think of any scenario where an inch and a half deep handy box would be code compliant for box fill?
 
Don't have an NEC in front of me, but I am reasonably sure that is not compliant, but maybe that is a plug recept not allowed.
 
Let me expand since we know that a 3x2x1-1/2" "handybox" cannot be used with any devices using 12 or 14 awg wire.

NEC Table 314.16(A) shows us that the box has a capacity of 7.5 cu/in.

The maximum number of conductors on the chart are: 14awg -3 and 12awg -3. This means that the ground, one white and one black and you are done. If you attempt to add a switch or receptacle, you are now over. If you run 14/3 wire you are over before you even think about a device. The box can only be used on the end of a circuit because you can't even come in with one 14/2 and leave to another box with 14/2. Basically they are good for fixtures where no devices will be in the box.
Screen Shot 2019-10-27 at 21.54.46.png
 