• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

40

cda

Sawhorse 123
Joined
Oct 19, 2009
Messages
20,963
Location
Basement
New building

New fire sprinkler system

During fire sprinkler plan review and field inspection

How do you handle the requirement to maintain all pipe to "40 degrees F"
 
cda, you don't have to address that except at the inspection.

The requirement is to "maintain" the temperature. Since you can't maintain what hasn't been constructed there's nothing to do during plan review if the building is intended to be heated. And, when inspecting, if the hvac inspection shows that the unit is operational, that's about it.

On the other hand, if the piping is in weird places you can question how heat will be provided in that space. For a typical lay-in-ceiling-with-insulation-on-the-roof there's nothing to worry about since the heated space below the ceiling will leak up into the interstitial space. But if they add batts or blankets to the tile and duct everything, then its worth asking. Years ago when I did sprinkler reviews, I'd ask occasionally - especially if the designer/contractor has a less than stellar reputation or is an unknown.
 