Shouldn’t be doing it but when I perform residential service upgrade inspections, I can’t be shutting off the power. I have to be mindful of what is going on in the dwelling. LA County had a rule that inspectors are not allowed to remove dead fronts. Many inspectors require the permittee to be on hand to do that. More likely is that the dead front is removed and there is nobody there to meet the inspector. It sits there wide open and energized for days waiting for an approval that didn’t happen. The corrections are completed and the panel is left wide open a second time as the process repeats..
Then there’s the inspectors that do not inspect behind a dead front. Another thing is that when the contractor has someone there to remove the dead front, they were often not qualified to open a bottle of beer, much less a service panel. I preferred to be alone and I have tools. If I couldn’t get in the panel, the inspection failed.
The point is that the handle tie is an impotent appendage. The tie supposes that the point of the new code is merely to open two breakers at the same time and then the chore is completed. Handle ties elsewhere in use are not removed after serving the initial purpose.