5A Beam Protection

Frank Karp

Member
Joined
Oct 20, 2011
Messages
13
Location
Rhode Island
First time doing a 3-story, 5A hotel - wow. We have most of it figured out, but can't find a 1 hour assembly to protect a primary steel beam. All 3 UL assemblies show steel/conc composite deck. We have plywood floor sheathing with 3/4" concrete topping using UL No. L570. Where else can I search? Or am I missing something? Must be fairly common. Thanks.
 
Most of the steel fit within the floor/ceiling assembly Builder Bob - a few deeper beam do not. I'm looking at Table 601 differently now after your question. If my floor assembly is 1 hour rated, is all the structure (primary and secondary) protected? I was thinking we needed to protect primary beams separately within the envelope. Thanks.
 
So my challange remains finding a 1 hour rated assembly/encasement for a steel beam (usually with a 2x nailer for the joist hangers and subfloor support/attachment) under plywood subfloor having a 3/4" concrete topping. Nothing in UL (that I found.) GA BM 1137 comes a bit closer, but still a ways off. Maybe AWC's National Design Standard for some type of equivilency guidance? Anywhere other sources out there?
 