• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

6.4.6.3.2 Pendent Sprinklers. nfpa 13R

cda

Sawhorse 123
Joined
Oct 19, 2009
Messages
20,963
Location
Basement
I know it has an "RRRRRRRRRRR" in it, but felt the question could be anywhere

NFPA 13R 2010

6.4.6.3.2 Pendent Sprinklers.

6.4.6.3.2.1 Pendent sprinklers shall be located at least 3 ft (914 mm) from obstructions such as ceiling fans and light fixtures unless the requirements of 6.4.6.3.4 are met.

Is the reason for the added distance away from an obstruction is because you are wetting more than the floor???? and the spray could be thrown off.
 
If you are comparing residential sprinklers to commercial sprinklers, then yes part of the reason for the added distance is because the performance criteria for residential sprinklers is to wet the walls. Also, residential sprinklers are similar to extended coverage sprinklers in that they are more sensitive to obstructions due to the increased coverage area. I believe that in NFPA 13, the obstruction rules for residential sprinklers are identical to those for extended coverage sprinklers.
 