60 second dry pipe trip test

cda

SAWHORSE
Joined
Oct 19, 2009
Messages
20,962
Location
Basement
When the 60 second trip test is required is it

A. Time it from when you open the inspector test till you get water there

Or

B. from the inspector test is opened , and time it from the dry pipe valve actually trips till you get water at the inspector test

Any Nfpa 13 section to support???
 
NFPA13 2007 edition

24.2.3.2.2* The test shall measure the time to trip the valve

and the time for water to be discharged from the inspector’s

test connection. All times shall be measured from the time the

inspector’s test connection is completely opened.

24.2.3.2.2.1 Dry systems calculated for water delivery in accordance

with 7.2.3.6 shall be exempt from any specific delivery

time requirement.
 