Once again, saw this and thought we could have a good discussion on this.
Wherever you have a junction box installed IAW 680.24, it also states under 680.3 that other articles apply for junction box support per 314.23.
When I read this, I understand that the support for the box must be with threaded conduit which eliminates using PVC for this application into the threaded portion of the junction box. Using a threaded pvc connection then gluing the pvc into the connection does not meet the requirements of 314.23(E).
In my opinion, proper support and compliance can be accomplished by running pvc then converting over to a threaded metallic raceway such as RMC as it transitions from UG to above.
1) Does anyone even enforce this?
2) Does anyone agree with my opinion?
Most of the wet niche fixtures that we see are PVC and have a conduit connection that gets glued anyway so the full length cannot be RMC anyway.
What say you....????????
Wherever you have a junction box installed IAW 680.24, it also states under 680.3 that other articles apply for junction box support per 314.23.
When I read this, I understand that the support for the box must be with threaded conduit which eliminates using PVC for this application into the threaded portion of the junction box. Using a threaded pvc connection then gluing the pvc into the connection does not meet the requirements of 314.23(E).
In my opinion, proper support and compliance can be accomplished by running pvc then converting over to a threaded metallic raceway such as RMC as it transitions from UG to above.
1) Does anyone even enforce this?
2) Does anyone agree with my opinion?
Most of the wet niche fixtures that we see are PVC and have a conduit connection that gets glued anyway so the full length cannot be RMC anyway.
What say you....????????