Show me where it is code compliant to install 1/2" nominal OSB or Plywood on a roof deck with a rafter span of 16" O.C.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
OK, now we are getting somewhere.I ASSUME you mean rafters 16" OC, not rafter span...or 16" sheathing span anyway....(well 14.5", but lets not get crazy)
View attachment 12186
Table R803.1 is for "lumber sheathing". It does not apply to wood structural panel sheathing, for which spans are covered in R803.2.2. Florida has amended R803.2.2 and has its own table; the unamended IRC R803.2.2 just refers you to Table R503.2.1.1(1).R803.1 and Table R803.1 set a minimum thickness of 5/8 sheathing for a 24" span, yet Table 503.2.2.2(1) shown above allows 7/16" at 24" O.C. without edge clips. This is a conflict in the code and the more restrictive applies, therefore, if you have trusses at 24" O.C., you must use 5/8" sheathing.
So Florida is messed up?Table R803.1 is for "lumber sheathing". It does not apply to wood structural panel sheathing, for which spans are covered in R803.2.2. Florida has amended R803.2.2 and has its own table; the unamended IRC R803.2.2 just refers you to Table R503.2.1.1(1).
Cheers, Wayne
Thanks Wayne. I was not being specific to Florida, but let me recap your answer.Table R803.1 is for "lumber sheathing". It does not apply to wood structural panel sheathing, for which spans are covered in R803.2.2. Florida has amended R803.2.2 and has its own table; the unamended IRC R803.2.2 just refers you to Table R503.2.1.1(1).
Cheers, Wayne
Yes....Is that what Chat GPT gave you?Thanks Wayne. I was not being specific to Florida, but let me recap your answer.
Lumber Sheathing, as listed in R803 would be for individual boards, not engineered plywood or OSB which are typically in 4'x8' sheets. So when I built a covered porch in 1989 and used 1-1/2' T&G so the underside would have better aesthetics, I was using lumber sheathing, not structural sheathing.
On the other hand, wood structural panel sheathing would be the OSB and plywood sheets that we typically see.
Therefore 803.2.2 specifically for roof sheathing points back to R503.2.1.1(1) which, although is under Floor Sheathing, applies to Roof Sheathing.
Does that sound correct as an explanation?
No, Florida only refers back to R503 for identification and grading. Florida has its own minimum structural panel sheathing table in 803 which is based on wind zone and exposure level. Florida does not refer back to 503 for roof sheathing spans.So Florida is messed up?
No, that is what I gave me.Yes....Is that what Chat GPT gave you?
Just busting you a bit..and seeing if you were still testing that stuff....the lumber vs. sheet goods clarified it a bit and Florida amending their own Table sealed the deal...No, that is what I gave me.
Still testing out the AI for sure. It can be a real pain in the butt sometimes and there are accuracy issues so sometimes I just create the outline myself.Just busting you a bit..and seeing if you were still testing that stuff....the lumber vs. sheet goods clarified it a bit and Florida amending their own Table sealed the deal...