705.5 Horizontal continuity.
Fire walls shall be continuous from exterior wall to exterior wall and shall extend at least 18 inches (457 mm) beyond the exterior surface of exterior walls.
Exceptions:
1. Fire walls shall be permitted to terminate at the interior surface of combustible exterior sheathing or siding provided the exterior wall has a fire-resistance rating of at least 1 hour for a horizontal distance of at least 4 feet (1220 mm) on both sides of the fire wall. Openings within such exterior walls shall be protected by fire assemblies having a fire protection rating of not less than ¾ hour.
2. Fire walls shall be permitted to terminate at the interior surface of noncombustible exterior sheathing, exterior siding or other noncombustible exterior finishes provided the sheathing, siding, or other exterior noncombustible finish extends a horizontal distance of at least 4 feet (1220 mm) on both sides of the fire wall.
3. Fire walls *****shall be permitted to terminate at the interior surface of noncombustible exterior sheathing***** where the building on each side of the fire wall is protected by an automatic sprinkler system installed in accordance with Section 903.3.1.1 or 903.3.1.2.
Situation....3 story wood frame VB apartment building, 13R (mostly).....Common apartment facilities (exercise, offices, etc...) seperated out by firewall (NFPA13 on that side).....Building(s) sheathed with OSB except for maybe an 18" strip of Densglas at firewall termination..... Plan review was done before I got here.....Seems to meet exception 3 even though I do not beleve that is the intent....any input? Is having a strip of noncombustible sheathing just as wide as the firewall the intent of Exception 3?
Fire walls shall be continuous from exterior wall to exterior wall and shall extend at least 18 inches (457 mm) beyond the exterior surface of exterior walls.
Exceptions:
1. Fire walls shall be permitted to terminate at the interior surface of combustible exterior sheathing or siding provided the exterior wall has a fire-resistance rating of at least 1 hour for a horizontal distance of at least 4 feet (1220 mm) on both sides of the fire wall. Openings within such exterior walls shall be protected by fire assemblies having a fire protection rating of not less than ¾ hour.
2. Fire walls shall be permitted to terminate at the interior surface of noncombustible exterior sheathing, exterior siding or other noncombustible exterior finishes provided the sheathing, siding, or other exterior noncombustible finish extends a horizontal distance of at least 4 feet (1220 mm) on both sides of the fire wall.
3. Fire walls *****shall be permitted to terminate at the interior surface of noncombustible exterior sheathing***** where the building on each side of the fire wall is protected by an automatic sprinkler system installed in accordance with Section 903.3.1.1 or 903.3.1.2.
Situation....3 story wood frame VB apartment building, 13R (mostly).....Common apartment facilities (exercise, offices, etc...) seperated out by firewall (NFPA13 on that side).....Building(s) sheathed with OSB except for maybe an 18" strip of Densglas at firewall termination..... Plan review was done before I got here.....Seems to meet exception 3 even though I do not beleve that is the intent....any input? Is having a strip of noncombustible sheathing just as wide as the firewall the intent of Exception 3?