I'm having trouble understanding when 713.12 would be applicable. Per section 713.5, the shaft shall have continuity per 707.5. 707.5 states:
Fire barriers shall extend from the top of the foundation or floor/ceiling assembly below to the underside of the floor or roof sheathing, slab or deck above and shall be securely attached thereto.
So if the shaft must be continuous between the floor and the structure above, when would you ever not enclose the top? Would this only apply if you stopped short of the last floor in the building?
Fire barriers shall extend from the top of the foundation or floor/ceiling assembly below to the underside of the floor or roof sheathing, slab or deck above and shall be securely attached thereto.
So if the shaft must be continuous between the floor and the structure above, when would you ever not enclose the top? Would this only apply if you stopped short of the last floor in the building?