I started looking the cda's post, and agreed with how confusing Chapter 7 can be at times, so I thought I would point out what confuses me about 2018 IBC Section 717.5.4.1 Corridors.
1- The is a subsection to 717.5.4 Fire partitions.
2- Duct and air transfer openings the penetrate fire partitions shall be protected with a listed fire damper.
3- There are 4 exceptions to this including one for a corridor. Follow exception 1, fire damper not required.
4- 717.5.4.1 Corridors
5- Duct and transfer openings that penetrate corridors shall be protected with dampers. Okay, not well defined, but we can still move forward.
6- Number 1 says a corridor damper shall be provided blah, blah, blah. Yea, this one throws me off. What is a corridor damper? It's not defined in the IMC. Is it a smoke damper? Fire damper? Radiation damper? The IBC has a definition that simply calls it a "listed device." Blah, blah, blah goes on to say that this "corridor damper" is required where corridor ceilings are constructed as required for the corridor walls per 708.4 exception 3. Doesn't that make the corridor ceiling a fire partition? If don't fire partitions require a fire damper at a duct penetration? Why not say fire damper instead of corridor damper?
7- Number 2 says a ceiling radiation dampers shall be provided blah, blah, blah. Ahh, a defined term. However the rest is confusing. Blah, blah, blah goes on to say this this is applicable to floor-ceiling and roof-ceiling assemblies per 708.4 exception 2. Looks to me that 708.4 exception 2 is not specific to floor-ceiling and roof-ceiling assemblies. As a matter of fact, it doesn't even make mention of these assemblies, only of the lower membrane of a corridor ceiling (which as shown above could be a fire partition) and the corridor wall membrane (which is a fire partition). So, this tells me that Number 2 is only applicable where a floor-ceiling or roof-ceiling is included in the corridor dasign. For those other designs, I suppose it's a corridor damper?
8- Number 3 says a smoke damper shall be provided (no blah, blah, blah this time) in duct penetrations of corridors that are required to have smoke and draft control doors only. Aren't Group I-2 and I-3 the only places where this could be applicable? If so then the two exceptions here would only apply to corridor conditions in Group I-2 and I-3, not in any R condition.
Feedback is welcome, clarification is encouraged. Perhaps next time we can discuss shaft options for Groups I-2 and I-3 under Section 717.6.1?
1- The is a subsection to 717.5.4 Fire partitions.
2- Duct and air transfer openings the penetrate fire partitions shall be protected with a listed fire damper.
3- There are 4 exceptions to this including one for a corridor. Follow exception 1, fire damper not required.
4- 717.5.4.1 Corridors
5- Duct and transfer openings that penetrate corridors shall be protected with dampers. Okay, not well defined, but we can still move forward.
6- Number 1 says a corridor damper shall be provided blah, blah, blah. Yea, this one throws me off. What is a corridor damper? It's not defined in the IMC. Is it a smoke damper? Fire damper? Radiation damper? The IBC has a definition that simply calls it a "listed device." Blah, blah, blah goes on to say that this "corridor damper" is required where corridor ceilings are constructed as required for the corridor walls per 708.4 exception 3. Doesn't that make the corridor ceiling a fire partition? If don't fire partitions require a fire damper at a duct penetration? Why not say fire damper instead of corridor damper?
7- Number 2 says a ceiling radiation dampers shall be provided blah, blah, blah. Ahh, a defined term. However the rest is confusing. Blah, blah, blah goes on to say this this is applicable to floor-ceiling and roof-ceiling assemblies per 708.4 exception 2. Looks to me that 708.4 exception 2 is not specific to floor-ceiling and roof-ceiling assemblies. As a matter of fact, it doesn't even make mention of these assemblies, only of the lower membrane of a corridor ceiling (which as shown above could be a fire partition) and the corridor wall membrane (which is a fire partition). So, this tells me that Number 2 is only applicable where a floor-ceiling or roof-ceiling is included in the corridor dasign. For those other designs, I suppose it's a corridor damper?
8- Number 3 says a smoke damper shall be provided (no blah, blah, blah this time) in duct penetrations of corridors that are required to have smoke and draft control doors only. Aren't Group I-2 and I-3 the only places where this could be applicable? If so then the two exceptions here would only apply to corridor conditions in Group I-2 and I-3, not in any R condition.
Feedback is welcome, clarification is encouraged. Perhaps next time we can discuss shaft options for Groups I-2 and I-3 under Section 717.6.1?