[F] 903.2.11.1.1 Opening dimensions and access.
Openings shall have a minimum dimension of not less than 30 inches (762 mm). Such openings shall be accessible to the fire department from the exterior and shall not be obstructed in a manner that fire fighting or rescue cannot be accomplished from the exterior.
Another jurisdiction that I am helping out
Open parking structure. The first tier has a mesh panel over the ventilation openings. Local FD says this is a violation of 903.2.11.1.1 and the structure needs to be sprinkled because the mesh covering interferes with the fire fighting and rescue operations.
the opening on Baker street on tier one are going to be covered with decorative mesh and tiers two and three openings will have decorative window frames...... it is our opinion that as designed this facility does not have adequate open ventilation to remove the heat and toxic gasses created from a single car fire let along multiple cars on fire. In addition, the 1st Street and Baker Avenue sides are obstructed in a manner that fire fighting and rescue cannot be accomplished from the exterior
I believe they are overreaching since the mesh panels could be easily breached with the equipment they carry. Sure it might take more than hand tools but what is an obstruction to a fire fighter? They breach locked solid wood or metal doors. I have seen access panels installed along walls that need to be removed for FD access, decorative block that can be knocked out in a few hits and many other scenarios acceptable to other departments.
What do you think?
Openings shall have a minimum dimension of not less than 30 inches (762 mm). Such openings shall be accessible to the fire department from the exterior and shall not be obstructed in a manner that fire fighting or rescue cannot be accomplished from the exterior.
Another jurisdiction that I am helping out
Open parking structure. The first tier has a mesh panel over the ventilation openings. Local FD says this is a violation of 903.2.11.1.1 and the structure needs to be sprinkled because the mesh covering interferes with the fire fighting and rescue operations.
the opening on Baker street on tier one are going to be covered with decorative mesh and tiers two and three openings will have decorative window frames...... it is our opinion that as designed this facility does not have adequate open ventilation to remove the heat and toxic gasses created from a single car fire let along multiple cars on fire. In addition, the 1st Street and Baker Avenue sides are obstructed in a manner that fire fighting and rescue cannot be accomplished from the exterior
I believe they are overreaching since the mesh panels could be easily breached with the equipment they carry. Sure it might take more than hand tools but what is an obstruction to a fire fighter? They breach locked solid wood or metal doors. I have seen access panels installed along walls that need to be removed for FD access, decorative block that can be knocked out in a few hits and many other scenarios acceptable to other departments.
What do you think?