• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

903.2.9.1 #4 Commercial Trucks and Buses

retire09

Silver Member
Joined
Feb 19, 2010
Messages
365
Location
Alaska
This requirement to provide sprinklers in repair garages for commercial trucks and buses over 5000sf is new.

I do not have a 2009 commentary and was wanting to know why this was added to the code.

Can someone explain the logic for this change?

Thanks
 
Automatic sprinklers may be required in repair

garages, depending on the quantity of combustibles

present, their location and floor area. In addition any

Group S-1 fire area intended for the repair of commercial

buses or trucks that exceeds 5,000 square feet

(464 m2) would require sprinklers. This is the same criteria

as Group S-1 occupancies and Group S-2

enclosed parking garages storing commercial buses

and trucks. Repair garages may contain significant

quantities of flammable liquids and other combustible

materials. These occupancies are typically considered

Ordinary Hazard Group 2 occupancies as defined in

NFPA 13. Portions of repair garages used for parts

cleaning using flammable or combustible liquids may

require automatic sprinkler protection. If quantities of

hazardous materials exceed the limitations in Section

307 for maximum allowable quantities per control

area, the repair garage would be reclassified as a

Group H occupancy.
 