Automatic sprinklers may be required in repair
garages, depending on the quantity of combustibles
present, their location and floor area. In addition any
Group S-1 fire area intended for the repair of commercial
buses or trucks that exceeds 5,000 square feet
(464 m2) would require sprinklers. This is the same criteria
as Group S-1 occupancies and Group S-2
enclosed parking garages storing commercial buses
and trucks. Repair garages may contain significant
quantities of flammable liquids and other combustible
materials. These occupancies are typically considered
Ordinary Hazard Group 2 occupancies as defined in
NFPA 13. Portions of repair garages used for parts
cleaning using flammable or combustible liquids may
require automatic sprinkler protection. If quantities of
hazardous materials exceed the limitations in Section
307 for maximum allowable quantities per control
area, the repair garage would be reclassified as a
Group H occupancy.