Mech
REGISTERED
2015 IBC
0 hour rated floor assembly
The owner is looking to install a few access hatches to provide maintenance access from the floor above into the ceiling / floor space below. The 5 ft tall ceiling space is above refrigerated rooms with insulated metal panel ceilings and will house ductwork and piping.
Is a fire rated door required in the floor assembly and if so, what is the minimum rating?
Section 711.3 Nonfire-resistance-rated floor and roof assemblies directs me to 711.3.2 Continuity which directs me to Section 712.
Section 712.1.13 Openings. Vertical Openings for floor fire doors and access doors shall be permitted where protected by Section 712.1.13.1 or 712.1.13.2 (The code commentary states that floor fire door assemblies must be installed in fire-resistance-rated floors and nonfire-resistance-rated floors.)
Section 712.1.13.1 Horizontal fire door assemblies. Horizontal fire door assemblies used to protect openings in fire-resistance rated horizontal assemblies shall be tested in accordance with NFPA 288, and shall achieve a fire-resistance rating not less than the assembly being penetrated. Horizontal fire door assemblies shall be labeled by an approved agency. The label shall be permanently affixed and shall specify the manufacturer, the test standard and the fire-resistance rating.
712.1.13.2 Access Doors
I did not think this applies.
Thanks.
0 hour rated floor assembly
The owner is looking to install a few access hatches to provide maintenance access from the floor above into the ceiling / floor space below. The 5 ft tall ceiling space is above refrigerated rooms with insulated metal panel ceilings and will house ductwork and piping.
Is a fire rated door required in the floor assembly and if so, what is the minimum rating?
Section 711.3 Nonfire-resistance-rated floor and roof assemblies directs me to 711.3.2 Continuity which directs me to Section 712.
Section 712.1.13 Openings. Vertical Openings for floor fire doors and access doors shall be permitted where protected by Section 712.1.13.1 or 712.1.13.2 (The code commentary states that floor fire door assemblies must be installed in fire-resistance-rated floors and nonfire-resistance-rated floors.)
Section 712.1.13.1 Horizontal fire door assemblies. Horizontal fire door assemblies used to protect openings in fire-resistance rated horizontal assemblies shall be tested in accordance with NFPA 288, and shall achieve a fire-resistance rating not less than the assembly being penetrated. Horizontal fire door assemblies shall be labeled by an approved agency. The label shall be permanently affixed and shall specify the manufacturer, the test standard and the fire-resistance rating.
712.1.13.2 Access Doors
I did not think this applies.
Thanks.