LGreene
REGISTERED
People ask me all the time if it's ok to lock the door to the roof. Most facilities want to prevent access from the stairwell to the roof for safety reasons and to deter vandalism, and also want to prevent access from the roof to the stairwell for increased security. The codes seem to allow that unless the roof is used as occupied space, but I've read several articles lately about people who tried to get to the roof during a fire and found the door locked. Some of them died, one local woman was saved by a firefighter after she passed out at the door. On the other hand, I read an article a few months ago about a toddler who wandered up to the roof and fell off.
What type of lock do you prefer to see on a door to an unoccupied roof?
Here are some code excerpts for your reference:
NFPA 101 – 2006 Edition: 7.2.1.5.8 If a stair enclosure allows access to the roof of the building, the door to the roof either shall be kept locked or shall allow re-entry from the roof.
IBC-2003 and 2006: 1018.1 … For the purposes of 780 CMR 10.00, occupied roofs shall be provided with exits as required for stories. The required number of exits from any story, basement or individual space shall be maintained until arrival at grade or the public way.
What type of lock do you prefer to see on a door to an unoccupied roof?
Here are some code excerpts for your reference:
NFPA 101 – 2006 Edition: 7.2.1.5.8 If a stair enclosure allows access to the roof of the building, the door to the roof either shall be kept locked or shall allow re-entry from the roof.
IBC-2003 and 2006: 1018.1 … For the purposes of 780 CMR 10.00, occupied roofs shall be provided with exits as required for stories. The required number of exits from any story, basement or individual space shall be maintained until arrival at grade or the public way.