    Once an accessible elevator (or horizontal exit exception) is deemed required by 1009.2.1, is that elevator required to serve all levels of the building? Or only the floors that are four or more stories above the level of exit discharge? For sake or argument 7 story non-highrise building with same floor plan of each story, is it permissible to have the accessible elevator (or horizontal exit) only serve floors 5,6,&7?
    The 1009.2.1 commentary seems like the elevator is required to serve all levels but the base Code is slightly different.
    Thanks!
  2. ADAguy
    ADAguy Sawhorse
    Sep 11, 2013
    4,128
    394
    How much $ saved to by pass the lower floors? Cables still need to go 7 floors.
  3. e hilton
    e hilton Bronze Member
    Jul 2, 2014
    730
    169
    Save a lot, not needing call buttons on every floor, no sliding doors, etc.
  4. ADAguy
    ADAguy Sawhorse
    Sep 11, 2013
    4,128
    394
    Less resale value if not stopping at every floor, how do you propose to move furniture?
  5. JPohling
    JPohling Sawhorse
    Aug 16, 2011
    1,062
    122
    penny wise, pound foolish
    Msradell likes this.
  6. e hilton
    Jul 2, 2014
    730
    169
    I see lots of new 3 story apartment buildings without elevators. Stupid IMHO but common.
  7. Builder Bob
    Builder Bob Sawhorse
    Oct 17, 2009
    2,278
    350
    If it is provided, then it should serve all floors IMHO otherwise, you are creating a sense of discrimination by not allowing ALL people free access to all floors - plus I am sure the renters would be more reluctant to rent a space on a floor without ease of elevator for material movement
    #7 Builder Bob, Jan 15, 2020 at 1:56 PM
    Msradell and ADAguy like this.
  8. my250r11
    my250r11 Sawhorse
    Feb 16, 2015
    607
    179
    Same old Crappy story. Help me save money so i can make more money. Will pay for it's self in no time. If were me on one of the no access floors I would more than likely file a discrimination lawsuit, so long run cheaper to make it equal for all. JMHO.
  9. ADAguy
    ADAguy Sawhorse
    Sep 11, 2013
    4,128
    394
    Is this an apartment or office building?
  10. e hilton
    Jul 2, 2014
    730
    169
    Lets don’t forget ... the question was about code, not stupidity. No law against that.
    my250r11 and ADAguy like this.
  11. RLGA
    RLGA Sawhorse
    Oct 18, 2009
    1,890
    604
    You have to keep in mind that the elevator requirements of Chapters 10 and 11 serve completely different purposes.
    Chapter 10, specifically Section 1009, applies only to accessible means of egress--in other words, getting people with disabilities out of a building in an emergency.
    Chapter 11 addresses how people with disabilities can access all areas of the building that are required to be accessible.
    Per Section 1104.4, one accessible route must connect every accessible story. If the 7th story is required to be accessible, then an elevator is required (unless you really want to try a ramp all the way up). If all the stories below are required to be accessible, then the elevator must stop at each one of those stories. Since the elevator serves an accessible story above the 4th story, the elevator must be considered one of the required accessible means of egress and comply with Section 1009.4.
    Joe Engel and mark handler like this.
  12. Brian 2
    May 18, 2017
    9
    0
    OK staying on the topic of an accessible elevator and Code; lets change the question slightly to exempt it by using a horizontal exit exception instead (IBC 1009.2.1 exception 1). Does the horizontal exit need to be provided on every floor of the building or does the horizontal exit only need to be provided on floors 5 and above?
  13. RLGA
    RLGA Sawhorse
    Oct 18, 2009
    1,890
    604
    Section 1009.2.1, Exception 1, will only relieve you of the requirement to make the elevator an accessible means of egress—an elevator will still likely be required for compliance with accessible route requirements.
    If using this exception, a horizontal exit must be used on every accessible floor above the level of exit discharge. If the 1st story is the level of exit discharge, then the 2nd story and above must have horizontal exits. Any accessible story without a horizontal exit will require the elevator to comply with Section 1009.4.
    Whether the elevator serves as an accessible means of egress or not, two-way communications is required at each elevator landing for each accessible floor above the level of exit discharge.
    my250r11 likes this.
  14. ADAguy
    ADAguy Sawhorse
    Sep 11, 2013
    4,128
    394
    haven't answered this?
  15. Brian 2
    May 18, 2017
    9
    0
    Apartment vs office (R2 or B occupancy) does not matter. IBC 1009.2.1 applies to any building with an accessible floor 4 or more stories above the level of exit discharge regardless of occupancy classification.
    The IBC commentary supports RLGA's opinion above; horizontal exits would be required on all floors above level 1. I was curious if anyone was providing it on the top floors only.