Existing commercial space with ~14' ceilings (exposed truss roof).
There is existing 3/4" EMT secured to the bottom the the steel trusses with a junction box (4" sq) every 10'.
New rooms with 8' GWB ceilings were constructed under this EMT & junction boxes. Ceilings only have GWB, no walkways or platforms on top of the ceiling (not rated for storage).
I contend that the junction boxes are a wiring method and must be accessible; eg they are exposed, you don't have to damage the building to access them. Must be "accessible"-- not "readily accessible".
Inspector says they need to be accessible with a ladder? The distance between the top of the ceiling joists and the junction boxes ranges from 5' to 6'-6", so I don't even know that a ladder is required. Granted you will have to walk the joists, and if you need a ladder you will have to bring some plywood or use a Little Giant. But more to the point, I don't see what a ladder has to do with "accessible".
He says "move them to an accessible location" "that can be accessed with a ladder".
Is there any merit to this? I just don't see it in any version of the NEC. 300.15(A) in the 2017.
There is existing 3/4" EMT secured to the bottom the the steel trusses with a junction box (4" sq) every 10'.
New rooms with 8' GWB ceilings were constructed under this EMT & junction boxes. Ceilings only have GWB, no walkways or platforms on top of the ceiling (not rated for storage).
I contend that the junction boxes are a wiring method and must be accessible; eg they are exposed, you don't have to damage the building to access them. Must be "accessible"-- not "readily accessible".
Inspector says they need to be accessible with a ladder? The distance between the top of the ceiling joists and the junction boxes ranges from 5' to 6'-6", so I don't even know that a ladder is required. Granted you will have to walk the joists, and if you need a ladder you will have to bring some plywood or use a Little Giant. But more to the point, I don't see what a ladder has to do with "accessible".
He says "move them to an accessible location" "that can be accessed with a ladder".
Is there any merit to this? I just don't see it in any version of the NEC. 300.15(A) in the 2017.