Hello all,
2020 Building Code of NYS - A-3 Assembly Space - Two-story
I'm currently reviewing a proposed two-story house of worship (first floor and basement). Both floors are above the 3000 sq. ft. threshold to use exc. #1 of 1104.4. Both floors will be used for assembly space. Both assembly spaces have flat floors.
During my initial review I called out the need for an elevator (accessible route) between the 1st floor and basement. The architect came back by proposing fixed seating in both the first and basement floor assembly areas. Does the addition of fixed seating negate the need for an accessible route to each story? The code sections and definitions which may apply here are below:
1104.4 Multistory Buildings and Facilities
At least one accessible route shall connect each accessible story, mezzanine and occupied roofs in multilevel buildings and facilities.
Exception #2 – Stories, mezzanines or occupied roofs that do not contain accessible elements or other spaces as determined by Section 1107 or 1108 are not required to be served by an accessible route from an accessible level.
Section 1108 Special Occupancies
1108.2 Assembly Area Seating - A building, room or space used for assembly purposes with fixed seating shall comply with Sections 1108.2.1 through 1108.2.5.
1108.2.1 Services - If a service or facility is provided in an area that is not accessible, the same service or facility shall be provided on an accessible level and shall be accessible
Element (Def. per ICC A117.1-2009) – An architectural or mechanical component of a building, facility, space or site.
Facility (Def. per BCNYS) - All or any portion of buildings, structures, site improvements, elements and pedestrian or vehicular routes located on a site.
Fixed Seating (Def. per BCNYS) - Furniture or fixture designed and installed for the use of sitting and secured in place including bench-type seats and seats with or without backs or armrests.
The architect is stating that each floor contains the same elements/facilities (assembly spaces, bathrooms, coffee areas, etc.) and as such an accessible route is not required.
Has anyone come across this scenario before? I'm getting hung up on the "accessible element" portion of 1104.4 exc. #2 as the basement does contain accessible bathroom facilities, diaper changing tables, hi/low drinking fountains, accessible sinks, etc. Any insight would be greatly appreciated. Thanks.
Side note - We do NOT enforce the ADA standards, only the ICC A117.1-2009.
2020 Building Code of NYS - A-3 Assembly Space - Two-story
I'm currently reviewing a proposed two-story house of worship (first floor and basement). Both floors are above the 3000 sq. ft. threshold to use exc. #1 of 1104.4. Both floors will be used for assembly space. Both assembly spaces have flat floors.
During my initial review I called out the need for an elevator (accessible route) between the 1st floor and basement. The architect came back by proposing fixed seating in both the first and basement floor assembly areas. Does the addition of fixed seating negate the need for an accessible route to each story? The code sections and definitions which may apply here are below:
1104.4 Multistory Buildings and Facilities
At least one accessible route shall connect each accessible story, mezzanine and occupied roofs in multilevel buildings and facilities.
Exception #2 – Stories, mezzanines or occupied roofs that do not contain accessible elements or other spaces as determined by Section 1107 or 1108 are not required to be served by an accessible route from an accessible level.
Section 1108 Special Occupancies
1108.2 Assembly Area Seating - A building, room or space used for assembly purposes with fixed seating shall comply with Sections 1108.2.1 through 1108.2.5.
1108.2.1 Services - If a service or facility is provided in an area that is not accessible, the same service or facility shall be provided on an accessible level and shall be accessible
Element (Def. per ICC A117.1-2009) – An architectural or mechanical component of a building, facility, space or site.
Facility (Def. per BCNYS) - All or any portion of buildings, structures, site improvements, elements and pedestrian or vehicular routes located on a site.
Fixed Seating (Def. per BCNYS) - Furniture or fixture designed and installed for the use of sitting and secured in place including bench-type seats and seats with or without backs or armrests.
The architect is stating that each floor contains the same elements/facilities (assembly spaces, bathrooms, coffee areas, etc.) and as such an accessible route is not required.
Has anyone come across this scenario before? I'm getting hung up on the "accessible element" portion of 1104.4 exc. #2 as the basement does contain accessible bathroom facilities, diaper changing tables, hi/low drinking fountains, accessible sinks, etc. Any insight would be greatly appreciated. Thanks.
Side note - We do NOT enforce the ADA standards, only the ICC A117.1-2009.