• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Accessible Stair Width - To Handrail vs. To Wall

fj80

Sawhorse
Joined
Jan 18, 2016
Messages
230
Location
Virginia
2015 IBC

1009.3 states that accessible stairs must have a clear width of 48" between handrails. Exception #2 says "The clear width of 48 inches between handrails is not required in buildings equipped throughout with an automatic sprinkler system..."

So if a sprinkler system is provided, does that mean the width of the accessible stairs is 48" from wall to wall, or does the width default to the standard width in Section 1011.2 (44" min or as based on occupant load)?
 
Yes but, what if it is to be considered an accessible stair vs an egress stair?
Stairs are not part of the accessible route, therefore, they cannot be considered accessible. For accessible means of egress, the width is not adjusted when considered an accessible means of egress and the building is sprinklered.
 