Every restroom, regardless of occupancy group, is required to be accessible. An accessible urinal is not required in women's restrooms.Hi
in a class E, if I’m having more than one toilet room on the same floor, do i need in each room an accessible toilet and an accessible urinal?
You are correct. Although it doesn't mention Group B, Exception 1 to Section 1109.2 does allow a private restroom accessed only from a private office to not be accessible.I believe a private office toilet room in a "B" is the only exception, unless that's changed recently with newer codes.
Existing or new, what is the scope of work?Hi
in a class E, if I’m having more than one toilet room on the same floor, do i need in each room an accessible toilet and an accessible urinal?
Don't agree. Toilet rooms accessed through a private office are not exempt from being accessible but alternatives are allowed for door swing, water closet height, grab bars, and lavatory height, knee and toe clearances. Everything else is required to comply with accessibility requirements.
newExisting or new, what is the scope of work?
All New facilities shall be accessible.
In an existing facility, not all restrooms need to be.
Not enough information.
It makes sense to gang them in two rooms, M/F, not five seperate rooms.So let’s say I’m making 5 toilet rooms on the same floor I will need to have 5 accessible toilets? Does this makes sense?
if im having 2 toilet rooms in one floor both for Male and per the occupancy i only need one HC why do i need now more?It depends on what the definition of "clustered" is...and what a single location is. Clustered on one floor? In one building? In one town? Steveray quotes one of the poorest code sections ever written.
E blum could take those same 5 toilets, put them in a single toilet facility, and only one compartment would need to be accessible. It does not make a lot of sense.
Regarding the original question, urinals are not required in the model code that we use (2012 I.P.C.). they may be used as a substitution for the required water closets, with certain restrictions.
GPE
basically my question is, is there anyway to have an exception on that????"Because" the code says so?
can the building inspector overwrite the iBC Code? if there is a justification? and what do yoy think can be accepted as a good justification?Up to AHJ to accept your justification.