1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Accessible windows?

Discussion in 'Accessibility' started by Yikes, Mar 2, 2012.

  1. Yikes

    Yikes Gold Member

    Joined:
    Nov 2, 2009
    Messages:
    1,398
    Likes Received:
    152
    In California, ona covered multifamily dwelling unit that is to be accessible, hw does this affect the types of windows that we use?

    1. Do the window controls, latches, etc, need to be within 48" of the floor?

    2. Is a casement window with a crank considered accessible? Or does the crank disqualify us because it requires "grasping"?

    3. What about a window that has a pull-out latch, like a slider - -is this OK?
     
  2. mark handler

    mark handler Sawhorse

    Joined:
    Oct 25, 2009
    Messages:
    10,143
    Likes Received:
    711
    A4.12.2 Window Hardware. Windows requiring pushing, pulling, or lifting to open (for example, double-hung, sliding, or casement and awning units without cranks) should require no more than 5 lbf (22.2 N) to open or close. Locks, cranks, and other window hardware should comply with 4.27.

    4.27 Controls and Operating Mechanisms.

    4.27.1 General. Controls and operating mechanisms required to be accessible by 4.1 shall comply with 4.27.

    4.27.2 Clear Floor Space. Clear floor space complying with 4.2.4 that allows a forward or a parallel approach by a person using a wheelchair shall be provided at controls, dispensers, receptacles, and other operable equipment.

    4.27.3* Height. The highest operable part of controls, dispensers, receptacles, and other operable equipment shall be placed within at least one of the reach ranges specified in 4.2.5 and 4.2.6. Electrical and communications system receptacles on walls shall be mounted no less than 15 in (380 mm) above the floor. Appendix Note

    EXCEPTION: These requirements do not apply where the use of special equipment dictates otherwise or where electrical and communications systems receptacles are not normally intended for use by building occupants.

    4.27.4 Operation. Controls and operating mechanisms shall be operable with one hand and shall not require tight grasping, pinching, or twisting of the wrist. The force required to activate controls shall be no greater than 5 lbf (22.2 N).

    http://www.windowease.com/

    http://www.milgard.com/milgard-advantages/smarttouch-window-lock.asp

    http://handicaphomemods.blogspot.com/2011/02/adauniversal-design-accessible-easy.html
     
  3. Yikes

    Yikes Gold Member

    Joined:
    Nov 2, 2009
    Messages:
    1,398
    Likes Received:
    152
    Mark, thanks for the research. If I understand you correctly, California Building Code Title 24 (chapter 11A for apartments) is silent on this subject as it relates to windows, but we can look to the ADA Guidelines for practical advice even though ADa does not apply to private dwellings. Is this correct?
     
  4. mark handler

    mark handler Sawhorse

    Joined:
    Oct 25, 2009
    Messages:
    10,143
    Likes Received:
    711
    Yes the California Building Code is silent on this subject, as is the Fair Housing Architectural Guidelines.

    There are no accessibility code requirements for private dwellings.
     
  5. Big Mac

    Big Mac Gold Member

    Joined:
    Oct 22, 2009
    Messages:
    563
    Likes Received:
    0
    Where operable windows are provided in areas that are required to be accessible in accordance with Sections 1107.5.1.1, 1107.5.2.1, 1107.5.3.1, 1107.5.4, 1107.6.1.1, 1107.6.2.1.1, 1107.6.2.2.1 and 1107.6.4.1, at least one window in each room shall be accessible and each required operable window shall be accessible. 2009 IBC, Section 1109.12.1.
     
  6. mark handler

    mark handler Sawhorse

    Joined:
    Oct 25, 2009
    Messages:
    10,143
    Likes Received:
    711
    We do not have Chapter 11 in California
     
  7. KZQuixote

    KZQuixote Sawhorse

    Joined:
    Nov 9, 2010
    Messages:
    499
    Likes Received:
    1
    Hi Folks,
    Given that 5 LBS is the maximum operating force for accessible windows, is there any allowance for breakway force? With most windows the weatherstripping grips the sash to some extent until the sash gets moving.
    Thanks in Advance.
    Bill
     
  8. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    3,464
    Likes Received:
    312
    Hmmm? When is a window a door if it is above grade, is it an operable part? If so then 5lbs would be it.
     
  9. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    2,012
    Likes Received:
    221
    Don't think they make windows that have controls and operating mechanisms that does not require tight grasping, pinching, or twisting of the wrist. None of the ones in post #2 comply.
     