A little confusion here about Accessory use and the plumbing fixture count--does accessory use areas count towards the plumbing fixture count?
I've always been able to add fractional numbers of fixtures for each use, then round up to the next integer for the sum.
Juliet, I'd say it depends on the accessory use.
For example, we often design R-2 apartment complexes with A-3 recreation / community rooms for the exclusive use of residents to have their own gatherings. These rooms are accessory to the dwelling units.
At most we have 1 or 2 single-accommodation toilet rooms serving these community spaces, just for convenience.
The idea here is that if a resident needs to use the restroom, they all have the ability to return to their own nearby apartment. In practice, most residents will likely use the bathroom in their own apartment prior to visiting the community room.
In this situation, the AHJ utilizes their authority under (California/Uniform Plumbing Code) Table 422 footnote 7, and sections 1.8.7 and 301.3 to assign the community spaces an occupant load of zero for purposes of determining minimum # of fixtures.
I've been doing this for years, and have never had an AHJ require toilet rooms for community spaces intended for private use.
If, on the other hand, the apartment complex allowed the community space to be rented out to the general public, then it would be totally appropriate to provide the A-3 occupancy with its own restroom facilities.
what about visitors / client coming into office for meetings? The IBC does not recognize the concept non-simultanious use as far as I know.Yikes, I appreciate your common sense approach to this. Curious if you would expect the same approach of an office building with small meeting spaces. If the spaces are less than 750 sf and say 48 occupants, should the 48 occupants be included in the plumbing fixture calculation? Or could the same consideration be applied where the meeting space occupants would be the same as the offices?
At our own office design, we did as Tim suggested in post #6 - - we counted the conference room occupants s being in addition to the office space occupants. As Tim said, we have visitors that come to our office for presentations.Yikes, I appreciate your common sense approach to this. Curious if you would expect the same approach of an office building with small meeting spaces. If the spaces are less than 750 sf and say 48 occupants, should the 48 occupants be included in the plumbing fixture calculation? Or could the same consideration be applied where the meeting space occupants would be the same as the offices?