Here comes another one of my famously-dumb questions! (If this generates any interest, I'll try to provide some pictures)
The situation is an existing A-3 (theater) beneath a 'B' use on the second floor (two-story building). This is a c.1920 building (Type III), full dimension 2X14 joists with 3/4 T&G flooring, overlayed with 1/2 ULF. Non-sprinklered building.
The scope of the project is a change of use and complete renovation of the main floor A-3 to an A-2 (Restaurant / Bar). Designer has used the performance approach. There is a required 2-hour separation between occupancies, but there is no work being done on the second floor. Is there a way to create a 2-hour separation when the floor surface of the second floor (top side of the horizontal assembly) is not being addressed? The area in question has a number of existing plumbing penetrations (drains from 2nd floor restrooms) which would be "challenging" - to say the least - to deal with at this point.
Is it possible to build a structural ceiling beneath the existing floor/ceiling assembly (anchored to the existing 2-hour exterior walls) which would have the required 2-hour membrane?
The situation is an existing A-3 (theater) beneath a 'B' use on the second floor (two-story building). This is a c.1920 building (Type III), full dimension 2X14 joists with 3/4 T&G flooring, overlayed with 1/2 ULF. Non-sprinklered building.
The scope of the project is a change of use and complete renovation of the main floor A-3 to an A-2 (Restaurant / Bar). Designer has used the performance approach. There is a required 2-hour separation between occupancies, but there is no work being done on the second floor. Is there a way to create a 2-hour separation when the floor surface of the second floor (top side of the horizontal assembly) is not being addressed? The area in question has a number of existing plumbing penetrations (drains from 2nd floor restrooms) which would be "challenging" - to say the least - to deal with at this point.
Is it possible to build a structural ceiling beneath the existing floor/ceiling assembly (anchored to the existing 2-hour exterior walls) which would have the required 2-hour membrane?