Question: In a multi-story residential building where laundry rooms are located on each floor, do all laundry rooms need to be accessible if the accessible dwelling units are only on the first floor?
Answer: No, if the accessible dwelling units are only on the first floor and the laundry rooms are restricted by floor—meaning the first-floor laundry room is for first-floor residents only and the second-floor laundry room is for second-floor residents only—then only the first-floor laundry room needs to be accessible. An accessible route to the second-floor laundry room is not required in this scenario. This ensures that the accessibility requirements are met without unnecessary modifications to other floors.
As confirmed by this advisory:
Advisory 206.2.3 Multi-Story Buildings and Facilities Exception 4. Where common use areas are provided for the use of residents, it is presumed that all such common use areas “serve” accessible dwelling units unless use is restricted to residents occupying certain dwelling units. For example, if all residents are permitted to use all laundry rooms, then all laundry rooms “serve” accessible dwelling units. However, if the laundry room on the first floor is restricted to use by residents on the first floor, and the second floor laundry room is for use by occupants of the second floor, then first floor accessible units are “served” only by laundry rooms on the first floor. In this example, an accessible route is not required to the second floor provided that all accessible units and all common use areas serving them are on the first floor.
Answer: No, if the accessible dwelling units are only on the first floor and the laundry rooms are restricted by floor—meaning the first-floor laundry room is for first-floor residents only and the second-floor laundry room is for second-floor residents only—then only the first-floor laundry room needs to be accessible. An accessible route to the second-floor laundry room is not required in this scenario. This ensures that the accessibility requirements are met without unnecessary modifications to other floors.
As confirmed by this advisory:
Advisory 206.2.3 Multi-Story Buildings and Facilities Exception 4. Where common use areas are provided for the use of residents, it is presumed that all such common use areas “serve” accessible dwelling units unless use is restricted to residents occupying certain dwelling units. For example, if all residents are permitted to use all laundry rooms, then all laundry rooms “serve” accessible dwelling units. However, if the laundry room on the first floor is restricted to use by residents on the first floor, and the second floor laundry room is for use by occupants of the second floor, then first floor accessible units are “served” only by laundry rooms on the first floor. In this example, an accessible route is not required to the second floor provided that all accessible units and all common use areas serving them are on the first floor.