Under "repairs" of the Existing Building Code (FBC edition) says this:
607.1.1Receptacles.
Replacement of electrical receptacles shall comply with the applicable requirements of Section 406.4(D) of NFPA 70.
Section 406.4(D) of the NEC says this:
(D) Replacements. Replacement of receptacles shall comply
with 406.4(D)(1) through (D)(6), as applicable. Arc-fault
circuit-interrupter type and ground-fault circuit-interrupter
type receptacles shall be installed in a readily accessible location.
I am just going to show you (D)(4) since I am only talking about AFCI even though there is a GFCI component requirement too.
(4) Arc-Fault Circuit-Interrupter Protection. Where a receptacle
outlet is located in any areas specified in 210.12(A) or (B),
a replacement receptacle at this outlet shall be one of the
following:
(1) A listed outlet branch-circuit type arc-fault circuitinterrupter
receptacle
(2) A receptacle protected by a listed outlet branch-circuit
type arc-fault circuit-interrupter type receptacle
(3) A receptacle protected by a listed combination type arcfault
circuit-interrupter type circuit breaker
Exception No. 1: Arc-fault circuit-interrupter protection shall not be
required where all of the following apply:
(1) The replacement complies with 406.4(D)(2)(b).
(2) It is impracticable to provide an equipment grounding conductor
as provided by 250.130(C).
607.1.1Receptacles.
Replacement of electrical receptacles shall comply with the applicable requirements of Section 406.4(D) of NFPA 70.
Section 406.4(D) of the NEC says this:
(D) Replacements. Replacement of receptacles shall comply
with 406.4(D)(1) through (D)(6), as applicable. Arc-fault
circuit-interrupter type and ground-fault circuit-interrupter
type receptacles shall be installed in a readily accessible location.
I am just going to show you (D)(4) since I am only talking about AFCI even though there is a GFCI component requirement too.
(4) Arc-Fault Circuit-Interrupter Protection. Where a receptacle
outlet is located in any areas specified in 210.12(A) or (B),
a replacement receptacle at this outlet shall be one of the
following:
(1) A listed outlet branch-circuit type arc-fault circuitinterrupter
receptacle
(2) A receptacle protected by a listed outlet branch-circuit
type arc-fault circuit-interrupter type receptacle
(3) A receptacle protected by a listed combination type arcfault
circuit-interrupter type circuit breaker
Exception No. 1: Arc-fault circuit-interrupter protection shall not be
required where all of the following apply:
(1) The replacement complies with 406.4(D)(2)(b).
(2) It is impracticable to provide an equipment grounding conductor
as provided by 250.130(C).