We understand the exhaust and makeup air requirements during a fire event when the ANSUL system is activated (NFPA 96) under the IMC. However, are there any codes that require the nearest air handler to be shut down?
Interesting question I have to say no typically but if make-up is coming from adjoining space I would think it would be part of the shut down
How would an air handler suppling conditioned air to a kitchen interfere with the operation of an ANSUL system installed in a Type I hood?
I was thinking there used to be something in the code that permitted make-up air to be supplied from the HVAC system in the building rather than a make-up air unit. I've never seen it proposed or inspected something like that though.
The only issue with air movement is shutting down the make-up air and continuing to exhaust when ANSUL is discharging
Do the listing or the manufacturer's instructions say to shut down all sources of makeup air? NFPA 96 par. 8.3.2 only requires makeup air supplied internally through the hood to be shut down.
This video is a demo. Looks like there might not be a hood...but if there is a hood it is far away from the fire. I know a guy that was preparing to dismantle an ansul system when an idiot set it off. Damn near resulted in two fatalities.