Re: Air test on plasitc?
Public works test sanitary sewer lines with 5psi for 5 min., do you think I should tell them to stop?
I require an air test on the dwv, 5psi for 15 mins, code IPC312.3. allows it.
I do not allow any rubber caps with clamps, they have to use glue on caps and screw in plugs. When releasing the air, has to be at the air valve entry not at the cap or plug and I witness the release to make sure there's no fast one being pulled by the dude with the pony tail, tats and that ear thing that looks like you could hook a tow hook too.
At another municipality it was required by the chief to have a water head test, while I was employeed there four where done with only one being approved, the old rubber balloons never work, old and brittle, they always seems to fail. You can't leave them in the sun or they crack. It got to be where I would have to go back several times, eating up the day. Other issues where they had no source for water.