steveray
SAWHORSE
606.2 Clear Floor Space. A clear floor space complying
with Section 305.3, positioned for forward approach,
shall be provided. Knee and toe clearance complying
with Section 306 shall be provided. The dip of the overflow
shall not be considered in determining knee and
toe clearances.
305.3 Size. The clear floor space shall be 48 inches
(1220 mm) minimum in length and 30 inches (760 mm)
minimum in width.
606.2 only sends you to 305.3 not the whole of 305, and doesn't get you to the alcove section:
305.7 Alcoves. If a clear floor space is in an alcove or
otherwise confined on all or part of three sides, additional
maneuvering clearances complying with Sections
305.7.1 and 305.7.2 shall be provided, as applicable.
Bad code language or intentional?
with Section 305.3, positioned for forward approach,
shall be provided. Knee and toe clearance complying
with Section 306 shall be provided. The dip of the overflow
shall not be considered in determining knee and
toe clearances.
305.3 Size. The clear floor space shall be 48 inches
(1220 mm) minimum in length and 30 inches (760 mm)
minimum in width.
606.2 only sends you to 305.3 not the whole of 305, and doesn't get you to the alcove section:
305.7 Alcoves. If a clear floor space is in an alcove or
otherwise confined on all or part of three sides, additional
maneuvering clearances complying with Sections
305.7.1 and 305.7.2 shall be provided, as applicable.
Bad code language or intentional?