Here it is in the fire code. Basically, if it is signed as an exit it has to function as one.This only says exit are to be marked. Still it does not say when a door is not an exit it shall not be marked as an exit.
I did my internship with a local fire engineering firm. They are very reputable and work internationally. I was lucky to have the experience that I did there.Anyone suggest what purposes a door, much like those intended for egress, is intended for if not for egress? As a designer, I can just see the building officials reaction to "that door is not intended for egress, it's only for ventilation or the view (in a warehouse) or for Uber eats deliveries. Would you allow key key deadbolts even?
Here it is in the fire code. Basically, if it is signed as an exit it has to function as one.
I should clarify, this is only an option where the number and location of "exits" are constructed in excess of the code.We don't use the IFC here unless the IBC section that sends us there, such as for high racks. So as an inspector I guess I can't make them take down any exit signs on non complying exit doors.
Do you make them take an exit sign down on an existing building that never had any exit doors that would comply with the latest code?
So ok to have a stair in a building with 8" treads and 10" risers if not required for nor intended for the means of egress?I did my internship with a local fire engineering firm. They are very reputable and work internationally. I was lucky to have the experience that I did there.
I remember one saying that they had was that the proper interpretation of any code provision was the least restrictive, reasonable interpretation.
When building officials reject a less restrictive, but reasonable interpretation of the code, they cease being a regulator enforcing the law and become an autocrat enforcing their preference.
No...Stairs do not have the same languageSo ok to have a stair in a building with 8" treads and 10" risers if not required for nor intended for the means of egress?
I would think about this another way. If it is signed as an exit, one could conclude that it is intended for egress purposes and thus must comply. If you cite something like "convenience doors that are signed as an exit must function as an exit" many can read between the lines and see the other option is to just remove the sign.I looks like the code does not give me any power to make them take down an exit sign on a non conforming convenient door like a slider or a door that is screwed shut even in a brand new building (that already has the minimum complying exit doors). I think their should be a section to require this but I can't make one up.
You just said it, it doesn't conform as an exit= remove sign/make complaint.non conforming convenient door
The doors that I am talking about are not a means of egress.This section...If you really need one
1010.1 Doors. Means of egress doors shall meet the requirements
of this section. Doors serving a means of egress system
shall meet the requirements of this section and Section
1022.2. Doors provided for egress purposes in numbers
greater than required by this code shall meet the requirements
of this section.
Means of egress doors shall be readily distinguishable
from the adjacent construction and finishes such that the
doors are easily recognizable as doors.
Correct,,,they are not, so they are not allowed to look like one....The doors that I am talking about are not a means of egress.
I need would need a section number to put in my report to make them take the exit sign down.
The basic issue is means of egress components in excess of what is required and whether they have to comply with the requirements for means of egress. Can a door in an exterior wall inswing, be less than minimum height and width, have no hardware to open it, or otherwise not comply with the requirements for a door in the means of egress? Can a stair in addition to all that are required for m.o.e. have 10" risers and no handrails? Can a non-required corridor be 30" wide? And for accessibility, if I add a door for convenience from room A to B, can it be inaccesible, requiring a person with a disability to take a much more circuitous route? Seems discrimatory. (And the concept in a theatre that if a non-disabled person can go from seat to stage without leaving the auditorium and stage, than a person with a disability should also be able to do that, and it's in the standards with words I drafted decades ago.)
The idea of "intended" use, that as one thing is not intended for m.o.e. is a big black hole. If I can evade code requirements by saying a door is not intended for egress, I can as easily claim a stair is not intended for egress, or a toilet not intended to or it's normal uses, or a big room in a school is not intended for assembly. And we all know how diligent owners are in applying for a permit for change of use.
And from the designer's view, look at how much time is saved if all m.o.e. components, required or in addition to what is required, comply with the m.o.e. requirements.
Here is the commentary for that section:
SECTION 1010
DOORS, GATES AND TURNSTILES
1010.1 Doors. Means of egress doors shall meet the requirements
of this section. Doors serving a means of egress system
shall meet the requirements of this section and Section
1022.2. Doors provided for egress purposes in numbers
greater than required by this code shall meet the requirements
of this section.
Means of egress doors shall be readily distinguishable
from the adjacent construction and finishes such that the
doors are easily recognizable as doors. Mirrors or similar
reflecting materials shall not be used on means of egress
doors. Means of egress doors shall not be concealed by curtains,
drapes, decorations or similar materials.
The general requirements for doors are in this section
and the following subsections. The reference to Section
1022.2 is intended to emphasize that exterior exit
doors must lead to a route that will allow a path to a
public street or alley (see definition for “Public way”).
A door that is intended to be used for egress purposes,
even though that door may not be required by
the code, is also required to meet the requirements of
this section. An example may be an assembly occupancy
where four doors would be required to meet
the required capacity of the occupant load. But
assume the designer elects to provide six doors for
aesthetic reasons or occupant convenience. All six
doors must comply with the requirements of this section.
Doors need to be easily recognizable for immediate
use in an emergency condition. Thus, the code
specifies that doors are not to be hidden in such a
manner that a person would have trouble seeing
where to egress.
What is it intended for?Like I said this door I'm talking about is not intended for a means of egress.