I realize codes say fire doors are allowed to have an opening force greater than 5 lbs and even up to 15 lbs, but doesn't that trigger an automatic door opener? Interior or exterior door.
If an accessible path requires automatic opener for any door greater than 5 lbs opening force... therefore all fire doors on an accessible path must have automatic opener regardless of 15 lbs allowance. (Imagine individual offices served by a rated corridor.)
I don't believe they make a fire rated door than can be less than 5 lbs.
11B-404.2.9 Door and gate opening force. The force for pushing or pulling open a door or gate shall be as
follows:
1. Interior hinged doors and gates: 5 pounds (22.2 N) maximum.
2. Sliding or folding doors: 5 pounds (22.2 N) maximum.
3. Required fire doors: the minimum opening force allowable by the appropriate administrative authority, not to exceed 15 pounds (66.7 N).
4. Exterior hinged doors: 5 pounds (22.2 N) maximum.
If an accessible path requires automatic opener for any door greater than 5 lbs opening force... therefore all fire doors on an accessible path must have automatic opener regardless of 15 lbs allowance. (Imagine individual offices served by a rated corridor.)
I don't believe they make a fire rated door than can be less than 5 lbs.