This is from Ontario building code Division B, part 9:
-----------------------------------------------------------------------------------------------------------
Section 9.15. Footings and Foundations
9.15.1. Application
9.15.1.1. General (See Appendix A and A-9.4.4.6.)
(1) Except as provided in Articles 9.15.1.2. and 9.15.1.3., this Section applies to,
(a) concrete or unit masonry foundation walls and concrete footings not subject to surcharge,
(i) on stable soils with an allowable bearing pressure of 75 kPa or greater, and
(ii) for buildings of wood frame or masonry construction,
(b) wood frame foundation walls and wood or concrete footings not subject to surcharge,
(i) on stable soils with an allowable bearing pressure of 75 kPa or greater, and
(ii) for buildings of wood frame construction, and
(c) flat insulating concrete form foundation walls and concrete footings not subject to surcharge,
(i) on stable soils with an allowable bearing pressure of 75 kPa or greater, and
------------------------------------------------------------------------------------------------------------
Question:
Allowable bearing pressure is actually a defined term in Ontario building code, is it equivalent to SLS of soil bearing capacity in part 4? What is the safety factor for checking it against column loading?(ALL geo-technical reports in Ontario would provide SLS and ULS soil capacity)
-----------------------------------------------------------------------------------------------------------
Section 9.15. Footings and Foundations
9.15.1. Application
9.15.1.1. General (See Appendix A and A-9.4.4.6.)
(1) Except as provided in Articles 9.15.1.2. and 9.15.1.3., this Section applies to,
(a) concrete or unit masonry foundation walls and concrete footings not subject to surcharge,
(i) on stable soils with an allowable bearing pressure of 75 kPa or greater, and
(ii) for buildings of wood frame or masonry construction,
(b) wood frame foundation walls and wood or concrete footings not subject to surcharge,
(i) on stable soils with an allowable bearing pressure of 75 kPa or greater, and
(ii) for buildings of wood frame construction, and
(c) flat insulating concrete form foundation walls and concrete footings not subject to surcharge,
(i) on stable soils with an allowable bearing pressure of 75 kPa or greater, and
------------------------------------------------------------------------------------------------------------
Question:
Allowable bearing pressure is actually a defined term in Ontario building code, is it equivalent to SLS of soil bearing capacity in part 4? What is the safety factor for checking it against column loading?(ALL geo-technical reports in Ontario would provide SLS and ULS soil capacity)