We are in the process of designing a dementia care facility and in trying to calculate allowable building area, height, etc. I came across something I'd never noticed and wondered if there is something to it, or if it's just wishful thinking.
Basically, what we'd like to do is construct a 2-story Group I-2 facility as Type VA Sprinklered building. Adding Sprinklers usually means a height and story increase to the limits in Table 503. This is clearly stated in 504.2:
"...the value specified in Table 503 for maximum building height is increased by 20 feet and the maximum number of stories is increased by one."
However, in Exception 1 of 504.2 it indicates the following:
"Exception: The use of an automatic sprinkler system to increase building heights shall not be permitted for the following conditions:
1. Buildings, or portions of buildings, classified as a Group I-2 occupancy of Type IIB, III, IV or V construction."
This exception says nothing about "Stories" only "Height". So am I interpreting this correctly that so long as my building is under 50' tall (per limit on table 503) that I can building a 2-story Group I-2 occupancy building as a Type V-A Sprinklered structure?
Thanks in advance for any input.
We are in the process of designing a dementia care facility and in trying to calculate allowable building area, height, etc. I came across something I'd never noticed and wondered if there is something to it, or if it's just wishful thinking.
Basically, what we'd like to do is construct a 2-story Group I-2 facility as Type VA Sprinklered building. Adding Sprinklers usually means a height and story increase to the limits in Table 503. This is clearly stated in 504.2:
"...the value specified in Table 503 for maximum building height is increased by 20 feet and the maximum number of stories is increased by one."
However, in Exception 1 of 504.2 it indicates the following:
"Exception: The use of an automatic sprinkler system to increase building heights shall not be permitted for the following conditions:
1. Buildings, or portions of buildings, classified as a Group I-2 occupancy of Type IIB, III, IV or V construction."
This exception says nothing about "Stories" only "Height". So am I interpreting this correctly that so long as my building is under 50' tall (per limit on table 503) that I can building a 2-story Group I-2 occupancy building as a Type V-A Sprinklered structure?
Thanks in advance for any input.