Amenity storage building plumbing

Timothy M. Stone

REGISTERED
Joined
Mar 22, 2017
Messages
9
Location
Fargo,ND
I need help finding the following in the IBC: owner of existing (4) 36 plex site wants to
add a 1,400 s.f. amenity storage building (500 s.f. to store tenant bicycles, 150 s.f. for
tenants to stand in the winter and watch their dog potty, 700 s.f. for first come first
serve tenant storage compartments, 50 s.f. mech room. That said, in my mind this
all falls under Storage-1, and there is no reason to provide a plumbing at 1 per 100
for toilets and lav's per IBC. Seeing that the occupant load is about 5, for a 1,400
s.f. storage building with occupants using the building will most likely be there 20 - 35
mins., and in theory, occupants using the building are tenants with plumbing in their
respective leased residences. All that said, is there anything or place in the IBC
that backs me up here? Thanks !
 
Can you get there in 500ft?

403.3.3 Location of toilet facilities in occupancies other
than malls. In occupancies other than covered and open mall
buildings, the required public and employee toilet facilities
shall be located not more than one story above or below the
space required to be provided with toilet facilities, and the
path of travel to such facilities shall not exceed a distance of
500 feet (152 m).
 
# ~ #

Timothy M. Stone,

Which IBC edition are you using ?
Also, I assume that this "proposed" Accessory Use
structure is detached from the other structures, and
that there is enough clearances from the other
structures, and that the applicable Zoning ordinances
are satisfied.


# ~ #
 
& ~ &

**steveray** has provided the correct Code Section from the IPC.
The correlating Section from the `15 IBC is Section 2902.3.2.

Is the 500 ft. dimension and the "not more than one story above
or below" requirement satisfied in your application ?.......If these
two requirements are satisfied within your application, then IMO,
you would not be required to have an ADA compliant restroom
in your Accessory use structure.

I would submit a Code Review using Code Section 2902.3.2,
and brief statement of your analysis, then let them [ possibly ]
counter that if needed.


& ~ &
 