I was classifying most of the back of house as "Group B" Due to IBC 303.1.2
Maybe I’m missing something, but why are you using separated mixed occupancies for this building, doesn’t the building qualify for nonseparated occupancy? Building area is 11,160 s.f., construction type is Type IIB with sprinklers, Table 506.2 allowable area factor for A-5 is unlimited, B is 92,000 s.f. Table 504.3 allowable building height is 75’ for both A and B. So if the entire building is within the more restrictive 92,000 s.f. area limit for Business I don’t know why you’d use separated occupancies. If you used nonseparated occupancy you could get rid of the 1-hour occupancy separation.
Not to step on your toes, but here are a few unsolicited comments on the plan:
1. In the Function of Space color key, “Business” is misspelled.
2. On the plan, you show two blue notes that read “Business (Group B)”, in Point 1 in the code review notes you only list Assembly A-5. You later go on to mention separated occupancies, so I would have thought you would have listed Group B under Point 1 as well.
3. In the two wheelchair accessible stalls, the door should be placed diagonally opposite the toilet per dimensions in A117.1-2017 Table 604.9.3.1.
4. Regarding the three-compartment sink, health department where I work requires drain boards on both ends of the sink, might want to confirm what your health department requires, might be different if it’s only a warming kitchen.
5. For the transfer showers, confirm you have adequate floor space beyond the seat wall per A117.1-2017 608.2.1.2, looks a little tight.