• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

An average day

ICE

Moderator
Joined
Jun 23, 2011
Messages
9,802
Location
California concrete jungle
Gastitie CSST. I have written many corrections for exposed CSST such as is shown here. Apparently I have been wrong many times. I recently searched the installation instructions and did not find anything that would require protection of this CSST. I called Gastite and was advised that no protection is required for CSST that is indoors and exposed.



IMG_3410.JPG
 
Last edited:

ICE

Moderator
Joined
Jun 23, 2011
Messages
9,802
Location
California concrete jungle
It's strapped.....Where does the vertical gas line go?
The CSST extends through a ceiling and attic to a furnace.

I'm thinking that there must have been a time when the CSST had to be protected if less than 6' above the floor.

There definitly was a time when the electrical bonding jumper had to be a solid #6 conductor and now it can be stranded #6.
 
Last edited:

Pcinspector1

Platinum Member
Joined
Oct 28, 2009
Messages
3,804
Location
MID WEST
Looks like a compliant install, you even have the yelow tag on the connection piece, did you follow the yellow CCST to the bonding point?

Where's fluffy at?
 

Pcinspector1

Platinum Member
Joined
Oct 28, 2009
Messages
3,804
Location
MID WEST
The gas pipe does not have the #6 bonding jumper.

Rut row!

Theres usually a sediment trap or drip leg trap between the valve and flex pipe. But I have seen the trap omitted when using flex lines. Does Califorina have wet gas? or can the drip trap be omitted?
 

Joe.B

Registered User
Joined
Dec 4, 2020
Messages
407
Location
Myrtletown Ca
Rut row!

Theres usually a sediment trap or drip leg trap between the valve and flex pipe. But I have seen the trap omitted when using flex lines. Does Califorina have wet gas? or can the drip trap be omitted?
Where I'm at in northern California we have extremely dry gas conditions so we can omit the "drips" per CPC 1210.6 or CMC 1310.8, but the way I read it the sediment trap is still required when "not incorporated as part of the appliance." I rarely see anything installed without a sediment trap, even though they are often not installed correctly.
 

Inspector Gift

Sawhorse - Made in USA
Joined
Oct 17, 2009
Messages
401
Location
City of Sandy, Oregon
Joe B., Like you, we require sediment traps in our jurisdiction. (G2419.4)

We also do not allow the PTR pipe to have reverse slope, be trapped, and to discharge in a location that is "readily observable"... . (UPC 608.5, #8) (P2804.6.1, #7)
 

ICE

Moderator
Joined
Jun 23, 2011
Messages
9,802
Location
California concrete jungle
Our meter enclosures are generally accessible...What do yours look like?
Here is a before and after. The terminals are the supply side of the meter. The latch at the bottom is where Edison places a seal. Edison places a seal to thwart theft.

Both of these pictures have a violation.


DSCN1772.JPG


IMG_5231.JPG
 
Last edited:

ICE

Moderator
Joined
Jun 23, 2011
Messages
9,802
Location
California concrete jungle
This was presented as a rain-tight installation. The contractor stated that they do this all over southern California and this is the first time that it has been rejected. The inspector identified the material as duct sealant. The package or container has a UL mark on the label. The description that I found does mention preventing moisture from entering conduits, enclosures, etc. it also states for indoor use only.