an unenclosed exterior exit stair or ramp

sunyaer

REGISTERED
Joined
Apr 21, 2022
Messages
338
Location
Toronto
This is from OBC (Ontario Building Code) Division B part 3:
--------------------------------------------------------------------------------------------------------------------------------------
3.2.3.13. Protection of Exit Facilities
...
(2) If an unenclosed exterior exit stair or ramp could be exposed to fire from an opening in the exterior wall of the
building it serves, the opening in the exterior wall of the building shall be protected in conformance with the requirements
of Sentence (4) where the opening in the exterior wall of the building is within 3 m horizontally and,
(a) less than 10 m below the exit stair or ramp, or
(b) less than 5 m above the exit stair or ramp.
...
-------------------------------------------------------------------------------------------------------------------------------------

Is the "ramp" referred to in the above clause enclosed or unenclosed?
 
Unenclosed. Enclosed (an interior ramp) is required to be protected the same as an interior stair enclosure.
 