• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

an unenclosed exterior exit stair or ramp

sunyaer

BRONZE MEMBER
Joined
Apr 21, 2022
Messages
338
Location
Toronto
This is from OBC (Ontario Building Code) Division B part 3:
--------------------------------------------------------------------------------------------------------------------------------------
3.2.3.13. Protection of Exit Facilities
...
(2) If an unenclosed exterior exit stair or ramp could be exposed to fire from an opening in the exterior wall of the
building it serves, the opening in the exterior wall of the building shall be protected in conformance with the requirements
of Sentence (4) where the opening in the exterior wall of the building is within 3 m horizontally and,
(a) less than 10 m below the exit stair or ramp, or
(b) less than 5 m above the exit stair or ramp.
...
-------------------------------------------------------------------------------------------------------------------------------------

Is the "ramp" referred to in the above clause enclosed or unenclosed?
 
Unenclosed. Enclosed (an interior ramp) is required to be protected the same as an interior stair enclosure.
 